LittleM

Recommended Posts

Any HVAC people here or can one be recommended.  Green Township area.  My central AC has been running for a few hours now with no appreciable change in temperature reduction.  I am thinking a freon recharge or new condenser (one I have is really old).

Link to comment
Share on other sites

I had the same issue as JimC last year.  Replaced the capacitor which was only a couple of bolts and 2 wires I believe and I was back in business.  I knew that it had gone bad because the top of it had bulged out considerably compared to the one on my other unit that was right next to it.  It was a $10 part from GPS.

Link to comment
Share on other sites

52 minutes ago, Integracingsr said:

I had the same issue as JimC last year.  Replaced the capacitor which was only a couple of bolts and 2 wires I believe and I was back in business.  I knew that it had gone bad because the top of it had bulged out considerably compared to the one on my other unit that was right next to it.  It was a $10 part from GPS.

I've had that happen too, the telltale bulge.

Link to comment
Share on other sites

Precision Heating & AC is owned by a guy that posted often on NJH, and involved in NJSFSC in Sussex County. Hackettstown Oil recommends him. But, I never did anything with him. Good luck.

Steve ..... 973 398 6600

Link to comment
Share on other sites

refrigeration in general especially simple residential splits the problem can generally be divided into 3 categories 

 

1) Mechanical/Electrical  Ex. Dual cap/Run Cap, Grounded Compressor(might trip breaker or blow line voltage fuses if you have a fused disconnect) An actual Bad Condenser fan Motor(usually the cap will go first) Bad Indoor blower motor or run cap(do you feel air coming from your registers?)  Low voltage wise bad T-stat, coil on your contractor, lost your 24v (air handler lost power) or 2wire some how got nicked. All though you stated you have an old system some boards have 3-5amp ATC Fuses some have fused transformers with resettable fuses....

2) Air side. Again, is the indoor/evap motor running? Plugged Filter....plugged evap coil(ice  or lint/dirt/particulate)Anything blocking your return air? 

3) refrigeration: notice any frost or ice on the suction line at the condenser? Discharge line warm? Suction line cold(similar to a beer can) notice any oil on or around the condenser or line set(ref leak) although unlikely depending on your metering device fixed Orifice or TXV there could be a restriction TXV bulb lost contact TXV is malfunctioning(not responding to spring or build pressure) do you have a sight glass or liquid line drier? Bubbles in the sight glass could be a sign of leak or restrictions Liquid Line Drier can get restricted..... A lot of these a good technician will assess by doing both superheat and sub cooling if refrigerant loss or other issue isn’t obvious.....

Do you see any condensate? 

Edited by Swampy
Link to comment
Share on other sites

Even though it’s easy enough to change a capacitor I really don’t recommend somebody that doesn’t have any electrical experience or knowledge start sticking their hands around anything even if you’re pull the disconnect or the breaker it’s just not recommended.

 

 But if you suspect it’s the dual capacitor (And yes the telltale bulge but not always) Try to keep your microfarads the same probably a 35/5 or there about....But I would suggest stepping up from a 370VAC to a 440VAC it’s more robust.

For an older system like yours you can also look into a start assist which could be added relatively easy Supco makes one.

 

Link to comment
Share on other sites

Appreciate all the responses.  I have a guy coming - father-in-law of a poster here............

I'm only handy with a hammer.  I did look outside after a while and saw that the fan was not spinning, but there was air (not cold) flowing though the system.

Link to comment
Share on other sites

  • 2 weeks later...
Even though it’s easy enough to change a capacitor I really don’t recommend somebody that doesn’t have any electrical experience or knowledge start sticking their hands around anything even if you’re pull the disconnect or the breaker it’s just not recommended.
 
 But if you suspect it’s the dual capacitor (And yes the telltale bulge but not always) Try to keep your microfarads the same probably a 35/5 or there about....But I would suggest stepping up from a 370VAC to a 440VAC it’s more robust.
For an older system like yours you can also look into a start assist which could be added relatively easy Supco makes one.
 
Any homeoner can say start capacitor until its a bad transformer in your air handler.

Sent from my SM-N950U using Tapatalk

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...